运行6毫米swa旋转隔离器和位置

我的父母有一个热水浴缸安装(< 6月5 kw, 32 amp)。重要的储蓄如果SWA电缆运行之前,允许交付团队和电工完成所有在一个访问。我被赋予的任务运行电缆。我主管在DIY,然而,鉴于这涉及储蓄我不相信我已经说服到很简单。安装如下:(注意我只运行SWA电缆)。6毫米SWA电缆从车库铜供应通过32 amp MCB(目前第一名盾牌之后,主开关和30 ma RCD 40安培;这个供应洗澡已经断开,取而代之的是一个混合器淋浴,我将订购一英国将军32 a SP类型名盾牌和假设的快速交换电工当天)。车库的SWA电缆将铜、退出车库,然后终止在IP65 45 AMP旋转隔离器开关位于2米远的地方,热水浴缸(不知道为什么这不能是一个32 AMP隔离器?——也许他们将配合)。然后6毫米SWA电缆需要热水浴缸的隔离器(不是我的问题,只需要有足够的备用可用)。 I’ve also been asked to supply a 32mm ‘stuffing gland’ for the electrician on the day? I have no issue using cable cleats for the SWA to be fixed to the internal garage wall from the CU, drilling and exiting the garage. Then, for the remaining <15-meter run, I see the only viable option as using cable cleats to fasten the cable to the fence/fence base board as the whole section outside the rear of the garage and down to the hot tub location is concrete followed by patio for the last 5 meters. It’s a new fence and when I said about this approach I was advised to do as I’ve suggested or run the SWA cable along the top of a fence beam. I’ve been told to fasten the cable to the fence with a distance between cable cleats as roughly one every length of a screwdriver. I thought there were firm regulations on running SWA, so I was surprised that fastening to the fence or fence beam wasn’t seeming to be any issue. Also, to me, the only place the isolator can go is on the fence and my assumption would be this isn’t permitted? I was wondering if, in front of the fence, I fit some form of 10x10 fence post with a board at roughly knee height, which I can secure via a bolt down post support to the patio/concrete, (more than 2m away from the hot tub location) and this can be where the incoming supply cable comes off the fence, terminating at the isolator, with an outgoing supply tail then to the hot tub. Does all that sound acceptable? I basically don’t want to waste what will likely take me a day running cable and making an isolator location for it to be incorrect. Always had great advice on questions here, thanks!

从MyBuilder电工4答案

最佳答案

你好。
在短暂的浏览你的文章…听起来像你做一个好工作。只有我可以看到反射的填料压盖可能是隔离器(热水浴缸)饲料的负载。
还RCD你说在40级,这可能是在最大多样性一旦你添加额外保护一侧的热水浴缸。如果是这样的话我会查看还有什么这RCD保护和潜在的升级63和使用32 B型MCB。失败这一点,你可以把热水浴缸供应32一个银行分理处之前40 RCD(但总开关后发射)。你也不能埋葬SWA吗?
不管怎样,听起来好你在做什么,可能比一些电工。
最好的——迈克

2023 - 05 - 05 - t11:21:32 + 01:00

回答2023年5月5日

你与隔离器委员会提议对我来说听起来不错。你必须把它靠近栅栏,swa电缆运行,这样几乎没有电缆悬挂可以说从栅栏板。300毫米建议夹板间距。Ip65 45 amp隔离器安装人员提出建议。32毫米填料压盖screwfix几英镑,你需要单独的电缆入口一(它说10毫米,16毫米的电缆,但6毫米电缆)

2023 - 05 - 05 - t12:07:41 + 01:00

回答2023年5月5日

有很多因素需要考虑与SWA电缆布线热水浴缸。最大负载,电压降等等。我个人倒让一个专业的,你就安心安全并正确地完成。最好的建议。

2023 - 05 - 04 - t18:20:05 + 01:00

回答2023年5月4日

有些粗略,交给专业的,克雷加文表示

2023 - 06 - 04 - t15:35:02 + 01:00

回答4日6月2023年