中央供暖系统
楼下的散热器不工作
4间卧室(8散热器)。建于1975年,2013年我们买了。它的一个扩展属性。在2015年改变了锅炉。结合巴喜锅炉(楼上)n没有问题自去年当客厅散热器(扩展)停止工作。今年厨房散热器停止工作(9月)。叫做一个工程师带电£350,化学清洗然后平衡所有的散热器,然后几天后lockshield需要改变散热器锅炉旁边开始泄漏。但厨房散热器n楼下客厅散热器仍然没有工作。唯一是使厨房工作是关闭楼上散热器。即使这样的客厅散热器后厨房只是轻微的热。 Engineer said if we changed the boiler or radiator things would be same and we have to close radiators upstairs to make it work. Anyways we called another engineer. He charged again £350. He fitted a filter , balanced the system, cleaned the boiler as he said there is problem with the boiler. Then asked to switch off upstairs radiators for a day to make downstairs radiators work. At that time kitchen radiator got hot too but not living room one. We did that for half a day but it got so cold upstairs that had to switch them on at night. I asked him for how long needed to switch upstairs one off, he said may be for a week to make system up n running. It sounds rediculous though to switch off upstairs radiators for a week. Then he said boiler is fine , nothing wrong. Also said that living room radiator will not work as the pipes width is v narrow n as living room is too far from boiler so we need to install electric panel radiator. Anyways the next day boiler pressure went down many a time n I had to increase it. Then called him again n when he came in n tried to adjust he diagnosed that expression vessel is faulty n will need new one n he will fit it after 3 days. Anyways after he went away pressure is stable. Upstairs, thermostat of radiators I set on 2 to get heating downstairs. So main problem is still there. Second, towel rail gets v hot at 2 and so the hallway radiator but some radiators dont work at 2. Third heating is on continuously n to turn off we need to turn off off through the sensor. Last 2 problems have occured when last engineer had gone. What to do? We spent so much already , dont know why its happening and how much we further need to spend. Is boiler an issue and we need to change it? Balancing and cleaning of radiators have been done already. Thinking to get homecare cover of heating too as they may be able to sort it out as they would have set of engineers, not one.
5个答案MyBuilder供暖工程师
最佳答案
罗姆尼的新•2016年11月15日以来成员•34工作,100%积极的反馈
现代的房子,可怜的管道尺寸和设计,泵尺寸不足,膨胀水箱容量不足,系统污泥,损坏的管道工程,你需要找到一个合格的供暖工程师,不仅仅是气体安全的人,还一个合格的供暖工程师。
回答2020年12月26日
曼彻斯特•2019年3月5日以来的成员•21工作,100%积极的反馈
Powerflush不工作如果是10毫米管道工程都是帮助它进一步阻碍。如上所述,您可能需要管的一些系统。简单的鉴别方法就是如果散热器加热当其他散热器关闭系统不平衡或锅炉在额定生产热拉德。如果散热器不加热会阻塞管道工程,和盾/锁阻塞或卡住了。它不会泵如果其他散热器越来越热,一个或2。它不会膨胀水箱否则你会有问题与整个系统失去压力。不幸的是在这个游戏中有更多的人假装知道实际上讲的是卖给你一些东西,而不是解决问题。
回答2020年12月27日
你好,个人从你所说的听起来不锅炉问题听起来你有micrbore管道工程,你要么有堵塞或碎管(流或返回)如果你有来自铁路/廖堵塞的管道工程可以有,我真的不率化学冲,会更powerflush(一些工程师在微内径不喜欢这样做,我没有问题)其他然后拉德repiped
回答2020年12月26日
Clacton-On-Sea•2021年9月2日以来成员•14工作,100%积极的反馈
相关问题
- 散热器- 3工作,2不要!
我有一个新锅炉安装在我的公寓,但很多管道工程是8毫米和10毫米。有两个散热器不得到热……
- 管道堵塞和散热器不工作
我们有两个散热器在家里不工作,我们假定它是由于管道阻塞。我们有权力冲洗和…
- 楼下散热器不加热
我有一个3床中连栋房屋。当从恒温器打开暖气,楼下散热器仍然寒冷而…
- 低效的供暖散热器不工作体系
这是一个4间卧室(9散热器)西北。建于1975年,2013年我们买了。它的一个扩展属性。改变了……